A finned-tube exchanger is used to heat 2.36 m3/s of air (specific heat of 1006 J/kg C) at 1 atm from 15.55 to 29.44°C. Hot water enters the tubes at 82.22°C and the air flows across the tubes, producing an average overall heat transfer coefficient of 227 W/m2C. The total surface area of the exchanger is 9.29m2. Calculate the heat transfer rate (kw) and the exit water temperature.

Report
Question

Please briefly explain why you feel this question should be reported.

Report
Cancel

A finned-tube exchanger is used to heat 2.36 m3/s of air (specific heat of 1006 J/kg C) at 1 atm from 15.55 to 29.44°C. Hot water enters the tubes at 82.22°C and the air flows across the tubes, producing an average overall heat transfer coefficient of 227 W/m2C. The total surface area of the exchanger is 9.29m2. Calculate the heat transfer rate (kw) and the exit water temperature.